Advise to a shaker/accelerometer control system
Started by Ole September 18, 2006
"Tim Wescott" <tim@seemywebsite.com> wrote in message
news:v9WdnR_R5d0Az5LYnZ2dnUVZ_oudnZ2d@web-ster.com...
> How versatile are those things, and what sort of sampling rate can they > sustain?
----- Original Message ----- From: "Tim Wescott" <tim@seemywebsite.com> Newsgroups: comp.dsp,sci.engr.control Sent: Monday, September 18, 2006 7:14 PM Subject: Re: Advise to a shaker/accelerometer control system
4 KHz easily. What do you want to do?. If I know I can write a user program to do the application. If the function isn't built in. Sine waves, flyiing shears, on-the-fly cam profiles are easy. The user programs run synchronously with the closed loop routines do everything is deterministic. The controller has velocity, acceleration and jerk feed forwards along with derivative gains for the error in acceleration and jerk. The controller was designed to be able to do underdamped second order systems easily. The auto tuning also will tune first order or second order systems. Peter Nachtwey
news:UM-dnagdL7BEYZPYnZ2dnUVZ_qednZ2d@rcn.net...
> A voice-coil shaker is no more likely to have backlash than a woofer. > > The voice-coil signal probably needs little or no filtering, since the > table's inertial itself provides substantial filtering. It should not be > difficult to precede the amplifier with a simple filter if image > frequencies are a problem. > > I presume that the control system's is there to maintain appropriate > frequency, acceleration, or some profile with time. How does that > information get to the ADC? Is there an LVDT or accelerometer? Both? > > To measure amplitude, you will want to find the peak of the position > signal. If the input is quite sinusoidal, quadrature sampling can make > that easy, but not as easy as a very high sample rate. Sampling at 20 > times the table frequency would match the peak reading to the true peak > within 1.52%, worst case. (Ditto for acceleration read from an > accelerometer.) No anti-alias would be needed, since the system itself > would then reduce the image frequencies to an acceptable level > > In any event, follow Tim's advice (and read the papers on his website). > > Jerry
Thanks! Please clarify the first part to me - do you mean that a control loop isn't needed? The controls system is intended to maintain appropriate deflection and curve shape. I need to send a low distortion sinus signals of different frequencies and amplitudes to the shaker. I also need to send a haversine deflection pulse curve with a pulse width of 15 to 15 ms and a deflection of 10 to 1500 &#4294967295;m. The shaker is able to create deflections of +/- 2500 &#4294967295;m. The "position" information is recorded by the accelerometer and send back to the ADC - there is no LVDT involved. Sample rate is 4000 Hz and the highest frequency that the system will be exposed to is about 40 Hz i.e. sample rate is 100 times higher. Thanks, Ole
news:h9udneDJIq5WYJPYnZ2dnUVZ_tqdnZ2d@web-ster.com...
> Ole wrote: > >> Thanks, >> >> Is it possible to purchase an electronic copy of your book? (I live in >> Denmark and it takes a while to purchase books from "overthere" and I >> would like to get running immediately). >> >> Best regards >> Ole >> > I checked with Elsevier, who replied: > > "He can order directly from our web site and the order will be fulfilled > from our warehouse in the UK. > > www.books.elsevier.com/computereng" > > I hope this helps.
Will have a look at it today - thanks. Ole
"Peter Nachtwey" <pnachtwey@comcast.net> wrote in message
news:OOKdnW7JOJIs2pLYnZ2dnUVZ_qSdnZ2d@comcast.com...
> Good. Filters would just add phase delay. >
Actually by a second thought I think a digital highpass filter with a very low cutoff frequency will be neccesary to avoid DC drift from the accelerometer. I believe that a 1st order butterworth will do. What is the consequence of doing that?
>> the 3 dB frequency range for the system must be 0 - 100 Hz (e.g. the >> shaker must be able to follow a 30 Hz sinus). >> > This will be the hard part. Designing 100 Hz systems is not easy if there > is much mass. > If the amplitude doesn't have to change then consider a mechanical cam. >
Both the frequency and the amplitude does change - see my description in my answer to Jerry for further details.
>> The control signal is digital and can be a deflection, velocity or >> acceleration signal depending on what is easiest or best to use. >> > I would use position feedback and the accelerormeter. A submicron glass > scale would be good. >
Sorry for my unclear description - I do not have a postion or velocity sensor - only an accelerometer. What I meant was that the input signal can be either a deflection, velocity or an acceleration.
> Start with the requirements and then the mechanical design. The > mechanical design must be right or the motion controller doesn't have a > chance. > What is the amplitude of the stroke and moving mass? > Be aware that the acceleration increases with the square of the frequency. > >
Yep - at the highest frequencies the deflection isn't very high in my system so that shouldn't cause any problem.
>> What sort of control system should I use? > I would buy a motion controller that has both a position and accelerometer > interface. The motion controller should also have gains for higher order > derivatives and for feed forwards. >
Again I was a bit unclear - sorry. The system is already here consisting of the shaker, an accelerometer, a microcontroller board with a 16 bit DAC and a 24 bit ADC. I actually meeant the type of control loop (PID, PI or PD etc.).
> There is no way you will achieve your goals with just a PID, PI or PD. A > PI has no chance at all because there there will be no stability without > the derivatives. You must have feed forwards if you want to track > accurately and you should have higher order derivatives that use the > acceleration feedback so there are gains for errors in acceleration and > jerk. >
What kind of control loop implements a feed forward signal? Thanks, Ole
Ole wrote:
> "Jerry Avins" <jya@ieee.org> wrote in message > news:UM-dnagdL7BEYZPYnZ2dnUVZ_qednZ2d@rcn.net... >> A voice-coil shaker is no more likely to have backlash than a woofer. >> >> The voice-coil signal probably needs little or no filtering, since the >> table's inertial itself provides substantial filtering. It should not be >> difficult to precede the amplifier with a simple filter if image >> frequencies are a problem. >> >> I presume that the control system's is there to maintain appropriate >> frequency, acceleration, or some profile with time. How does that >> information get to the ADC? Is there an LVDT or accelerometer? Both? >> >> To measure amplitude, you will want to find the peak of the position >> signal. If the input is quite sinusoidal, quadrature sampling can make >> that easy, but not as easy as a very high sample rate. Sampling at 20 >> times the table frequency would match the peak reading to the true peak >> within 1.52%, worst case. (Ditto for acceleration read from an >> accelerometer.) No anti-alias would be needed, since the system itself >> would then reduce the image frequencies to an acceptable level >> >> In any event, follow Tim's advice (and read the papers on his website). >> >> Jerry > > Thanks! > > Please clarify the first part to me - do you mean that a control loop isn't > needed?
I don't know where "first part" ends. I didn't address the nature of the loop at all, only the input and output arrangement.
> The controls system is intended to maintain appropriate deflection and curve > shape. I need to send a low distortion sinus signals of different > frequencies and amplitudes to the shaker. I also need to send a haversine > deflection pulse curve with a pulse width of 15 to 15 ms and a deflection of > 10 to 1500 &#4294967295;m. The shaker is able to create deflections of +/- 2500 &#4294967295;m.
I take it then that the control system needs to compensate for variations of the voice-coil current/force relation and of suspension stiffness as functions of position, as surmised in my "P.S."
> The "position" information is recorded by the accelerometer and send back to > the ADC - there is no LVDT involved.
In reality, then, there is no position information, only doubly-integrated acceleration. The integrators will need to be "leaky" in order to avoid accumulation of DC error. How will you handle the haversine? Ver(x) = 1-cos(x); hav(x) = (1-cos(x))/2 = sin^2(x/2) and so has a substantial DC component. With only accelerometer feedback, that will be hard manage.
> Sample rate is 4000 Hz and the highest frequency that the system will be > exposed to is about 40 Hz i.e. sample rate is 100 times higher.
That is good. The choice of no filters was well justified. Jerry -- Engineering is the art of making what you want from things you can get. &#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;&#4294967295;
Ole wrote:
> "Peter Nachtwey" <pnachtwey@comcast.net> wrote in message > news:OOKdnW7JOJIs2pLYnZ2dnUVZ_qSdnZ2d@comcast.com... > > >>Good. Filters would just add phase delay. >> > > Actually by a second thought I think a digital highpass filter with a very > low cutoff frequency will be neccesary to avoid DC drift from the > accelerometer. I believe that a 1st order butterworth will do. What is the > consequence of doing that? >
It depends on where you put the filter, and what you do with the results. At issue is the fact that you are sensing acceleration but you want to control position -- you can't do that. To control position you'd have to integrate your accelerometer output twice, which would make you sensitive not only to the accelerometer offset, but also to the accelerometer drift. This is why Peter suggested that you monitor the position -- this makes up for the lack of absolute position and velocity information from the accelerometer. It does introduce the problem that you have to monitor the position relative to some frame of reference, which is a (literally) shaky proposition in a room with a shaker table. What I'd do would be to design a position estimator that uses the low-frequency content of the position measurement along with the high-frequency content of the accelerometer to get a good measurement -- this is a case where I'd consider doing a formal Kalman filter design, but doing the job intuitively is often more than good enough. This is also why Jerry suggested that you implement leaky integrators in your forward path -- assuming that your table is suspended so that it tends to return to the correct average position leaky integrators in your PID loop will guarantee that you don't try to push the table into the stratosphere. It still leaves you with the table seeking it's own level, but if that's good enough then go for it!
> >>>the 3 dB frequency range for the system must be 0 - 100 Hz (e.g. the >>>shaker must be able to follow a 30 Hz sinus). >>> >> >>This will be the hard part. Designing 100 Hz systems is not easy if there >>is much mass. >>If the amplitude doesn't have to change then consider a mechanical cam. >>
There are some pretty heavy issues with using cams in shaker tables. But you are correct that 100Hz will be -- uh -- interesting to attain.
> > Both the frequency and the amplitude does change - see my description in my > answer to Jerry for further details. >
You'll not only want to do your design carefully, but you'll want to pay close attention to integrator windup issues. Here your integrators will mostly be the mass of the table, but that's nothing to ignore. If you don't pay attention, you'll see yourself having severe overshoot problems. Probably the easiest and most common way to fix this is to calculate the command profile ahead of time such that it doesn't ask for more acceleration than the table is capable of, although I often prefer to build the relevant nonlinearities into the controller.
> > >>>The control signal is digital and can be a deflection, velocity or >>>acceleration signal depending on what is easiest or best to use. >>> >> >>I would use position feedback and the accelerormeter. A submicron glass >>scale would be good. >> > > Sorry for my unclear description - I do not have a postion or velocity > sensor - only an accelerometer. What I meant was that the input signal can > be either a deflection, velocity or an acceleration. >
You'll need to build the system to ignore the low-frequency content of the deflections & velocity commands, then.
> > >>Start with the requirements and then the mechanical design. The >>mechanical design must be right or the motion controller doesn't have a >>chance. >>What is the amplitude of the stroke and moving mass? >>Be aware that the acceleration increases with the square of the frequency. >> > Yep - at the highest frequencies the deflection isn't very high in my system > so that shouldn't cause any problem. >
You may find it causing problems at low frequencies, however, when you run out of room.
> >>>What sort of control system should I use? >> >>I would buy a motion controller that has both a position and accelerometer >>interface. The motion controller should also have gains for higher order >>derivatives and for feed forwards. >> > > Again I was a bit unclear - sorry. The system is already here consisting of > the shaker, an accelerometer, a microcontroller board with a 16 bit DAC and > a 24 bit ADC. I actually meeant the type of control loop (PID, PI or PD > etc.). > > >>There is no way you will achieve your goals with just a PID, PI or PD. A >>PI has no chance at all because there there will be no stability without >>the derivatives.
You should be able to build a stable system with a PI. Perhaps not one that gets you up to 100Hz, but a current command to the coil is essentially an acceleration command, and you're reading back acceleration. As long as you stay well within the bandwidth of the drive electronics and the accelerometer you should be fine. Even with a voltage feed to the coil a PI will stabilize, since your plant will look like a simple lowpass plus the accelerometer's bandwidth. But -- it'll almost certainly stabilize well below your desired bandwidth. None the less, were I working on this I'd start by getting it working with a PI controller or just a proportional controller, then do some bumps and some sine sweeps to get the plant transfer function. Then I'd use the _measured_ transfer function to (a) validate that my model was correct, (b) validate that the mechanical assembly was correct, and (c) use for all future control system design. Particularly with something like this where you're trying to get so much speed out of something so big (I assume it's big) the sine sweep will do a good job highlighting mechanical resonances that you'll need to dodge when you do the control system design.
>> You must have feed forwards if you want to track >>accurately and you should have higher order derivatives that use the >>acceleration feedback so there are gains for errors in acceleration and >>jerk. >> > > What kind of control loop implements a feed forward signal?
I don't believe that they've been given a formal name. "PID with feedforward" is probably the closest you'll come. -- Tim Wescott Wescott Design Services http://www.wescottdesign.com Posting from Google? See http://cfaj.freeshell.org/google/ "Applied Control Theory for Embedded Systems" came out in April. See details at http://www.wescottdesign.com/actfes/actfes.html
Tim Wescott wrote:
> Ole wrote: > >> Thanks, >> >> Is it possible to purchase an electronic copy of your book? (I live in >> Denmark and it takes a while to purchase books from "overthere" and I >> would like to get running immediately). >> >> Best regards >> Ole >> > I checked with Elsevier, who replied: > > "He can order directly from our web site and the order will be fulfilled > from our warehouse in the UK. > > www.books.elsevier.com/computereng" > > I hope this helps. >
And according to Elsevier UK: "Dear Tim, There are several academic bookstores in Denmark who would be happy to sell the book to your contact in Denmark. It depends where he is located in Denmark, but I would suggest following bookstores to whom we directly supply: www.polyteknisk.dk - Copenhagen www.universitetsbogladen.dk Copenhagen www.boghandel.sdu.dk - Odense www.stakbogladen.com - Arhus" -- Tim Wescott Wescott Design Services http://www.wescottdesign.com Posting from Google? See http://cfaj.freeshell.org/google/ "Applied Control Theory for Embedded Systems" came out in April. See details at http://www.wescottdesign.com/actfes/actfes.html