Scott L wrote:
> On Mar 16, 7:57 am, "Peter Nachtwey" <p...@deltacompsys.com> wrote: >> You can't use an >> accelerometer or other hardware so you should look into a higher order >> Butterworth filter or observer. The observer can be used to estimate >> the second derivative without the lag of a Butterworth filter. > > In my math doodlings, I wrote the second derivative as: > > (e[n] + e[n-2] - 2*e[n-1]) / dt^2 > > I.e., the typical finite difference approximation (obviously not > centered). Are you saying that's too naive in the presence of noise?
Differentiators have a gain that is proportional to frequency. They emphasize high-frequency noise to the point that it can dominate the signal. Digital or analog, their high-frequency responses are always limited on control applications. To the extent that their embodiment introduces delay, the proportional signal must also be delayed if the derivative is to apply at the same instant. For servos, this rules out sophisticated embodiments. Jerry -- Engineering is the art of making what you want from things you can get. &macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;
Scott L wrote:
> On Mar 16, 7:57 am, "Peter Nachtwey" <p...@deltacompsys.com> wrote: > >>You can't use an >>accelerometer or other hardware so you should look into a higher order >>Butterworth filter or observer. The observer can be used to estimate >>the second derivative without the lag of a Butterworth filter. > > > In my math doodlings, I wrote the second derivative as: > > (e[n] + e[n-2] - 2*e[n-1]) / dt^2 > > I.e., the typical finite difference approximation (obviously not > centered). Are you saying that's too naive in the presence of noise? >
Yes. You need to low-pass that to get a good answer. You can combine the differentiator and the low-pass, and you can cascade two such differentiators (you'll want to get the 1st-differentiator answer anyway). I'm feeling too lazy to go into depth here (it's in my book), but you're looking for a transfer function in the z domain that looks like: /(1-d)(z-1)\ 2 H_d(z) = | ---------- | \ z - d / (note that you could use two different roll-off frequencies and probably want to -- just using one and squaring the transfer function is another instance of laziness on my part). If you don't know z transforms, buy my book or look at http://www.wescottdesign.com/articles/zTransform/z-transforms.html. -- Tim Wescott Wescott Design Services http://www.wescottdesign.com Posting from Google? See http://cfaj.freeshell.org/google/ "Applied Control Theory for Embedded Systems" came out in April. See details at http://www.wescottdesign.com/actfes/actfes.html
On Mar 17, 6:18 am, Tim Wescott <t...@seemywebsite.com> wrote:
> Scott L wrote: > > On Mar 16, 7:57 am, "Peter Nachtwey" <p...@deltacompsys.com> wrote: > > >>You can't use an > >>accelerometer or other hardware so you should look into a higher order > >>Butterworth filter or observer. The observer can be used to estimate > >>the second derivative without the lag of a Butterworth filter. > > > In my math doodlings, I wrote the second derivative as: > > > (e[n] + e[n-2] - 2*e[n-1]) / dt^2 > > > I.e., the typical finite difference approximation (obviously not > > centered). Are you saying that's too naive in the presence of noise? > > Yes. You need to low-pass that to get a good answer. You can combine > the differentiator and the low-pass, and you can cascade two such > differentiators (you'll want to get the 1st-differentiator answer > anyway). I'm feeling too lazy to go into depth here (it's in my book), > but you're looking for a transfer function in the z domain that looks like: > > /(1-d)(z-1)\ 2 > H_d(z) = | ---------- | > \ z - d / > > (note that you could use two different roll-off frequencies and probably > want to -- just using one and squaring the transfer function is another > instance of laziness on my part). > > If you don't know z transforms, buy my book or look athttp://www.wescottdesign.com/articles/zTransform/z-transforms.html. > > -- > > Tim Wescott > Wescott Design Serviceshttp://www.wescottdesign.com > > Posting from Google? Seehttp://cfaj.freeshell.org/google/ > > "Applied Control Theory for Embedded Systems" came out in April. > See details athttp://www.wescottdesign.com/actfes/actfes.html
Hasn't anybody heard of phase advance? Simple undergrad stuff - come on...don't reinvent the wheel. F.
> introduces delay, the proportional signal must also be delayed if the > derivative is to apply at the same instant. For servos, this rules out > sophisticated embodiments. >
Delay??? You don't get delay from differentiation - noise problems yes and that's why it needs to be band limited. The main problem with too much phase-advance is that it causes an increase in high freq gain. This in turn leads to amplification of structural resonances (or other related problems). There is also a problem of crossing unity gain more than once. You need to draw this to see why but suppose you have k/s^2 .(1+st1)^3/(1+st2)^3 This gives a slope of -12db?octave then +6dB/octave then a -ve roll- off - 3 crossings (possibly) of 0dB.We then have 3 phase-margins!! F.
minfitlike@yahoo.co.uk wrote:
> On Mar 17, 6:08 am, Jerry Avins <j...@ieee.org> wrote: > To the extent that their embodiment >> introduces delay, the proportional signal must also be delayed if the >> derivative is to apply at the same instant. For servos, this rules out >> sophisticated embodiments. >> > Delay??? You don't get delay from differentiation - noise problems yes > and that's why it needs to be band limited. > The main problem with too much phase-advance is that it causes an > increase in high freq gain. This in turn leads to amplification of > structural resonances (or other related problems). There is also a > problem of crossing unity gain more than once. You need to draw this > to see why but suppose you have
You don't get delay from differentiation, but you do get delay from differentiators. In analog circuits, the delay is small. It is due to transistor effects and usually ignored.
That's analog. Try it with digital. The difference equation will include terms like z^-1. Those are delays.
> This gives a slope of -12db?octave then +6dB/octave then a -ve roll- > off - 3 crossings (possibly) of 0dB. We then have 3 phase-margins!!
Great! Notice that a one-sample delay at Fs/2 represents a 180 degree phase lag. Jerry -- Engineering is the art of making what you want from things you can get. &macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;
> Hasn't anybody heard of phase advance? Simple undergrad stuff - come > on...don't reinvent the wheel.
You can't use analog grease on a digital axle. Jerry -- Engineering is the art of making what you want from things you can get. &macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;
Yes, but forget about noise for now. The real enemy is quantizing. I see application every day where the feed back resolution is only 0.0001m but even if the feedback resolution is .00001m there is still problems. Assume the sample time is .001s and the resolution is .00001m then the best resolution on the acceleration is 10m/s^2 or a little over 1g. That isn't really usable for motion control. If you try to use the 0.00001m resolution you will be severely limited in how high the double derivative gain can be increased without the control output going wild. Low pass output filter will help only a little but not enough. Fortunately, most system can be modeled as having just one or two poles so a normal PID will do well enough until you start to push it to point where higher order un-modeled poles start to affect control. Then you must start identifying these higher frequency poles too and add higher order derivative gains the the controller so these poles can be placed somewhere safe. In the process you will need feedback to that can measure these gains directly or you need some sort of filter or observer that can estimate the higher order derivatives better than you can measure them directly. When noise is added the problem is even worse. Peter Nachtwey
-- snip --
> > > Hasn't anybody heard of phase advance? Simple undergrad stuff - come > on...don't reinvent the wheel. > > F. >
And how are you going to achieve this phase advance without either non-causal filtering or differentiators? Much of that 'simple undergraduate stuff' is simple because it aids teaching, not because it is unconditionally useful in the real world or even physically possible. Where it is physically possible, and sometimes useful, one has to be exquisitely aware of its limitations to keep oneself from applying it where it will do more harm than good. -- Tim Wescott Wescott Design Services http://www.wescottdesign.com Posting from Google? See http://cfaj.freeshell.org/google/ "Applied Control Theory for Embedded Systems" came out in April. See details at http://www.wescottdesign.com/actfes/actfes.html
On Mar 20, 1:44 am, Jerry Avins <j...@ieee.org> wrote:
> minfitl...@yahoo.co.uk wrote: > > On Mar 17, 6:08 am, Jerry Avins <j...@ieee.org> wrote: > > To the extent that their embodiment > >> introduces delay, the proportional signal must also be delayed if the > >> derivative is to apply at the same instant. For servos, this rules out > >> sophisticated embodiments. > > > Delay??? You don't get delay from differentiation - noise problems yes > > and that's why it needs to be band limited. > > The main problem with too much phase-advance is that it causes an > > increase in high freq gain. This in turn leads to amplification of > > structural resonances (or other related problems). There is also a > > problem of crossing unity gain more than once. You need to draw this > > to see why but suppose you have > > You don't get delay from differentiation, but you do get delay from > differentiators. In analog circuits, the delay is small. It is due to > transistor effects and usually ignored. > > > k/s^2 .(1+st1)^3/(1+st2)^3 > > That's analog. Try it with digital. The difference equation will include > terms like z^-1. Those are delays. > > > This gives a slope of -12db?octave then +6dB/octave then a -ve roll- > > off - 3 crossings (possibly) of 0dB. We then have 3 phase-margins!! > > Great! Notice that a one-sample delay at Fs/2 represents a 180 degree > phase lag. >
Of course but that's why you need to sample at least 10-20 times the max freq of interest. Digital costs - you don't get anything for nothing and besides - you always need to think first if a digital design is necessary. One of the problems today is the 'lets do it digital' blind school of engineering. I expect soon most engineers won't know how a transistor works. Anyway - delays are no problem if you sample high enough, if you cannot then you need to re-think but it helps even in digital control to think analogue. F.
> On Mar 20, 1:44 am, Jerry Avins <j...@ieee.org> wrote: >> minfitl...@yahoo.co.uk wrote: >>> On Mar 17, 6:08 am, Jerry Avins <j...@ieee.org> wrote: >>> To the extent that their embodiment >>>> introduces delay, the proportional signal must also be delayed if the >>>> derivative is to apply at the same instant. For servos, this rules out >>>> sophisticated embodiments. >>> Delay??? You don't get delay from differentiation - noise problems yes >>> and that's why it needs to be band limited. >>> The main problem with too much phase-advance is that it causes an >>> increase in high freq gain. This in turn leads to amplification of >>> structural resonances (or other related problems). There is also a >>> problem of crossing unity gain more than once. You need to draw this >>> to see why but suppose you have >> You don't get delay from differentiation, but you do get delay from >> differentiators. In analog circuits, the delay is small. It is due to >> transistor effects and usually ignored. >> >>> k/s^2 .(1+st1)^3/(1+st2)^3 >> That's analog. Try it with digital. The difference equation will include >> terms like z^-1. Those are delays. >> >>> This gives a slope of -12db?octave then +6dB/octave then a -ve roll- >>> off - 3 crossings (possibly) of 0dB. We then have 3 phase-margins!! >> Great! Notice that a one-sample delay at Fs/2 represents a 180 degree >> phase lag. >> > > Of course but that's why you need to sample at least 10-20 times the > max freq of interest. Digital costs - you don't get anything for > nothing and besides - you always need to think first if a digital > design is necessary.
First, note that "great!" was intended as sarcasm. Second, observe that the delay of a differentiator you can actually use is nearly independent of the sample rate. Although that applies to floating point also, it's a little easier to see with fixed point. If you sample fast enough, the short differentiator's output will usually be zero and sometimes |1|.
> One of the problems today is the 'lets do it digital' blind school of > engineering. I expect soon most engineers won't know how a transistor > works. > Anyway - delays are no problem if you sample high enough, if you > cannot then you need to re-think but it helps even in digital control > to think analogue.
Quantizing in time and magnitude forces one to modify analog techniques to a degree that can make them unrecognizable. Jerry -- Engineering is the art of making what you want from things you can get. &macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;&macr;